HMCP used as a feeder, but thermal magnetic down stream

Status
Not open for further replies.

adamscb

Senior Member
Location
USA
Occupation
EE
Forum,

I have 480v single-phasing coming into a 480/120v transformer that goes to a 120v/240v panel. If the panel has a 200A main circuit breaker (thermal magnetic), can I use an HMCP on the primary side of the transformer?

(Transformer is 50kVA).
 
No. There is no valid use for an HMCP (aka Mag Only, or officially, IT (Instantaneous Trip only) breaker) other than part of a LISTED FACTORY ASSEMLED COMBINATION STARTER. None.
 
Forum,

I have 480v single-phasing coming into a 480/120v transformer that goes to a 120v/240v panel. If the panel has a 200A main circuit breaker (thermal magnetic), can I use an HMCP on the primary side of the transformer?

(Transformer is 50kVA).

you can, but it won't meet code unless you put a real CB or fuses in as well.
 
Status
Not open for further replies.
Top