rivecar44
- Chicago IL, USA (MDW)
- Engineer
Please tell me the reasons why "OFF" is in the middle. Could it be HAO (i.e. transition from one control location to another without turning the system off)?
Because grandpa did it like that.Please tell me the reasons why "OFF" is in the middle. Could it be HAO (i.e. transition from one control location to another without turning the system off)?
You can get any combination of closed contacts that you want for a 3 position selector, but the set up you mentioned is the most common.Because the 3 position selector switches I usually see have a set of contacts that close when turned to the left, another set that close when turned to the right, and none when in the center.
The Hand mode often allows a start/stop/reverse station to have control, or it may simply start a system regardless of the system's condition. The Auto mode will run the system according to other inputs. Either way if you want to turn the system Off, and the Hand mode is next to the Auto mode, the system may start when you don't want it to while switching through the modes to get to the Off mode. That won't happen with the Off mode in the middle.Please tell me the reasons why "OFF" is in the middle. Could it be HAO (i.e. transition from one control location to another without turning the system off)?
Yeah, but if you want to smoothly transition between manual and PLC control a HAO sequence makes more sense.The Hand mode often allows a start/stop/reverse station to have control, or it may simply start a system regardless of the system's condition. The Auto mode will run the system according to other inputs. Either way if you want to turn the system Off, and the Hand mode is next to the Auto mode, the system may start when you don't want it to while switching through the modes to get to the Off mode. That won't happen with the Off mode in the middle.
Hadn't really thought about why before. Good question!
And if you do not want such a transition? Suppose you have a tank with a level switch, a pump, and piping with a strainer. Something is going on and the operator switches to Hand mode and operates the pump at the local control station. He discovers that there is a leaky gasket on the strainer and turns the pump off at the local station. The HAO switch at the main control panel is still in Hand. The tank is at a level where if the system is in Auto mode, the pump will start and spray fluid all over the place. If he switches from Hand to Off, he must go through the Auto position causing this to happen. Sure, the operator can do this, that, and the other to prevent it, but this is just an example.Yeah, but if you want to smoothly transition between manual and PLC control a HAO sequence makes more sense.
IMO, it should be made very obvious Hand vs Auto has been selected and not only by looking at selector switch positions. PLCs certainly make that easier.I can only remember one time I dealt with people who used HAO. I asked why and they said so that they wanted it to be more obvious if a switch was not in auto.
As well as different operating characteristics for the cam that actuates those contact blocks, or even an operator with maintained position one way and spring return the other way from center, though that would typically be more for something like jog off auto instead of hand off auto when it comes to describing the function - electrically they would basically be wired the same.You can get any combination of closed contacts that you want for a 3 position selector, but the set up you mentioned is the most common.
In the plant I did a lot of work at, the hand was only for lockout verification in most cases, and was spring return to center.As well as different operating characteristics for the cam that actuates those contact blocks, or even an operator with maintained position one way and spring return the other way from center, though that would typically be more for something like jog off auto instead of hand off auto when it comes to describing the function - electrically they would basically be wired the same.
Plant I've done a lot of work in often was Run (or sometimes maybe auto)/Off/CIP Left position being the "normal operating method whether automated or not beyond just turning the switch there and CIP (clean in place) was basically an auto position but let the CIP system control the item when needed during the cleaning process.In the plant I did a lot of work at, the hand was only for lockout verification in most cases, and was spring return to center.
You would go to the equipment, use the hand position to see the equipment run, go to the MCC and lockout the starter, and then return to the HOA to verify that the equipment would not run. If the motor was on a VFD, the hand would go to a separate input in the VFD that was set to run at 15hz. The hand position would bypass all interlocks with the exception of the overload relay in the starter bucket.
There were a few cases where they wanted to use the hand position to keep the equipment running and those did not have spring return. One example was the cooling water pumps on the reactors. The hand position was maintained on those so that in the event of a process control failure they could run the pumps in hand. There was an additional contact on those to put the temperature mixing valve to cooling water only.
If I remember right when working on Telco central office switchgear, their breaker ind. light logic was the opposite to industry standards. Red meant the breaker was closed while green meant breaker open. I guess it is what your reference is. Red (closed) means caution, load circuit is hot, while green (closed) means load circuit is hot and condition is a go or normal.Hard to say. Why do some places use red lights for running and others use green?
Square D and Allen Bradley had different standard colors for their ON pilots. We had a price adder if you wanted the other person's color from the factory. We gave away a lot of colored caps for the EC to field install.If I remember right when working on Telco central office switchgear, their breaker ind. light logic was the opposite to industry standards. Red meant the breaker was closed while green meant breaker open. I guess it is what your reference is. Red (closed) means caution, load circuit is hot, while green (closed) means load circuit is hot and condition is a go or normal.