Does Square D make a hold-down for a double pole QO breaker in an arbitrary location? As far as I can tell from the catalog, they only offer them for the upper right location.
If not, is there a generic alternative that can be used? With two double pole breakers left-right does putting a long cable tie around both breaker bodies really work?
This is for a system with PV and ESS and an MID; my understanding that the ESS interconnect breakers require a hold-down. Certainly if the ESS is operating in off-grid mode and you pop one of the ESS interconnect breakers off the bus, the bus terminals will be live unless the breaker is off.
Thanks,
Wayne