Hello,
On Wednesday, during a rain lighting and thunder my TV, house alarm system, house phone, A/C unit and garage opener lost power.
The TV, alarm system, A/C thermostat and house phone was fried or damage, and no longer work. My A/C unit (furnace) power wires to the unit was badly burnt/damage, but the unit fuse opened to protect the unit from damage. The garage opener was protect from power panel breaker.
All other loads in the house remain energized. I have to purchase new TV, phone, and alarm system from this issue. I am now buying individual surge protector for each wall outlet to protect for future surges.
Here is the gotcha. I have a http://sycomsurge.com/~sycomsur/images/products/SYC-T2 Series.pdf here is the installation at the panel to a 20amp fuse. http://prntscr.com/at49wl. This device should have protected the against voltage or current spikes. But looks like the green light is still on. I believe the unit is not working as it did not protect.
This same issue happened 5 months ago during another lighting, but all mentioned above appliances did not get fried or damage. I reset the breaker and it all worked fine.
I called American Homeshield and they sent an electrician to inspect what happen and he concludes the problem is with the underground service feeders from the electrical company transformer. He states the problem is the feeder conductors could be bad when lightening occur. I call the electrical company to inspect their box where the feeder conductors come from their transformer box and electrical company electrician states everything looks good.
I call another electrician for second opinion and he states he is 80% sure the feeder cables have an issue and recommends replacing the feeder cables. I tell him can you please at least megger the cables first to confirm the cables have an issue. He states, a megger will cost $1900. I tell him, I believe the problem is not with the cables but with the home surge protector not protecting the house appliances as it should.
So now I am calling the electrician who installed the home surge protector and the manufacture to let them know their device is not protecting appliances.
Lighting and thunder storms will occur, and not much I can do to protect against that, but I expect the surge protector to work. 2 times it did not work.
What do you think the problem may be?
Thank you, any comments are welcome.