This is a follow up to a post from Sept 24, 2004 regarding home automation systems. I made a comment in that post with respect to having to make some level of investment in time, product and/or test equipment to become experienced with working with home automation products.
In November of 2003 I installed a combination of (4) X-10 relay modules and addressable receptacles (all set to the same address) with a master switch at the front door and signal amplifier/repeater at a sub-panel in an 8000 sq. ft home. The system was controlling outdoor landscape lighting. The set-up worked fine for the first two months then began to fail. I returned to the job and re-tested all the equipment and it seemed to work fine. Another month goes by and the customer called me complaining that the system did not work. Return trip # 2 revealed that the master transmitter switch was defective. I didn't have a new one with me so I left a desk-top remote control which worked fine for about 3 months. On return trip # 3 I re-installed a new wall switch and hadn't heard from her in about 4 months.
Finally the call came and I was preparing to go out and make return call # 4 but first I called tech support. Their stand was that there was nothing wrong with their product and that the X-10 signal was being blocked due to noise being generated by some component like a computer or a TV. They wanted me to invest $ 300.00 in a signal analyser which I could not bring myself to do. So I purchased several noise reduction interface modules and made trip # 4 to install them on all wall outlets where computers or TV's were being used. The system worked fine for several months and died again. I then purchased some wall switches from a different manufacturer/distributor and went back out for return trip # 5. I was only able to get 3 out of 4 areas to respond to the signal. I then began hunting for a signal blocking source. It took about an hour but I finally found a large telephone switching mechanism and Lyncsys computer modem plugged into a receptacle in the basement. When I re-installed an noise reduction interface module at that location the problem was solved.
Long story short - "You gotta pay for your education when using this equipment!!!"
In November of 2003 I installed a combination of (4) X-10 relay modules and addressable receptacles (all set to the same address) with a master switch at the front door and signal amplifier/repeater at a sub-panel in an 8000 sq. ft home. The system was controlling outdoor landscape lighting. The set-up worked fine for the first two months then began to fail. I returned to the job and re-tested all the equipment and it seemed to work fine. Another month goes by and the customer called me complaining that the system did not work. Return trip # 2 revealed that the master transmitter switch was defective. I didn't have a new one with me so I left a desk-top remote control which worked fine for about 3 months. On return trip # 3 I re-installed a new wall switch and hadn't heard from her in about 4 months.
Finally the call came and I was preparing to go out and make return call # 4 but first I called tech support. Their stand was that there was nothing wrong with their product and that the X-10 signal was being blocked due to noise being generated by some component like a computer or a TV. They wanted me to invest $ 300.00 in a signal analyser which I could not bring myself to do. So I purchased several noise reduction interface modules and made trip # 4 to install them on all wall outlets where computers or TV's were being used. The system worked fine for several months and died again. I then purchased some wall switches from a different manufacturer/distributor and went back out for return trip # 5. I was only able to get 3 out of 4 areas to respond to the signal. I then began hunting for a signal blocking source. It took about an hour but I finally found a large telephone switching mechanism and Lyncsys computer modem plugged into a receptacle in the basement. When I re-installed an noise reduction interface module at that location the problem was solved.
Long story short - "You gotta pay for your education when using this equipment!!!"