Home Inspector question

Status
Not open for further replies.
wwhitney said:
Only if the hots come from different phases. In the NECH diagram, it appears they have 8 hots, 4 on each phase, and presumably the neutral is sized to 4 times the ampacity of the hots. So that is an MWBC. But you could use only hots from one phase, and size the neutral appropriately.

Cheers, Wayne
Same phase yes.
 
acwservices said:
Okay, I should know the answer to this, but for the life of me, I cannot locate a reference in the NEC. If someone could point me in the right direction, I would appreciate it. On a recent home inspection report, the home inspector cited "mutiple conductors improperly connected under the same screw on the neutrel bar." I see this quite a bit on inspection reports, and usually I can just remove one of the conductors, and move it to an empty hole on the neautrel bar. However, there are no empty spaces available on this panel. It is a Cutler Hammer, BR series, and even though the house is over 10 years old, the electrical system looks good overall. I don't know who the electrician was who wired this house when it was built originally, but he obviously took pride in workmanship. This electrical system looks so good overall that I want to be sure that there is a code violation before I recommend a costly repair to the seller.


yea but 10 years ago you could still terminate 2 nuetrl wires under one screw...so whats wrong with the install..another unlicensed HI doing electrical work..

edited: I was trying not to comment as you all know my feeling on HI doing electrical work..inspections of electrical systems is electrical work..
 
Last edited:
cschmid said:
yea but 10 years ago you could still terminate 2 neutral wires under one screw..

.

Actually, the panel label probably stated the neutral bar was only rated for 1 neutral.
As I recall, this section was added to the NEC because most guys weren't reading the label, and landing 2 neutrals, or neutral/EGC under 1 screw.
 
JohnJ0906 said:
Actually, the panel label probably stated the neutral bar was only rated for 1 neutral.
As I recall, this section was added to the NEC because most guys weren't reading the label, and landing 2 neutrals, or neutral/EGC under 1 screw.


Oh I agree with that assessment..I have never been big on terminating 2 neutrals on a lug..aI will add bars to my panel to achieve enough termination room..but I think it is an injustice to us as electricians that the panel manufacturer do not equip a panel with enough termination points..
 