Went to look at a EV charger install.
The Electrical required is a 40amp 240v circuit.
The unfortunate thing is the Town home only has a 60 amp service and is group metering.
The home has A/C (3 ton) and is about 1200 Sqft. all gas appliances. I calculate just under 60 amps load. So I told the lady a no go.
I get a call from her telling me that another Electrician says no problem we can do this with your 60amp. panel you have.
Question is do we ignore the calculations because we feel the actual load will never exceed the 60amp.
The Electrical required is a 40amp 240v circuit.
The unfortunate thing is the Town home only has a 60 amp service and is group metering.
The home has A/C (3 ton) and is about 1200 Sqft. all gas appliances. I calculate just under 60 amps load. So I told the lady a no go.
I get a call from her telling me that another Electrician says no problem we can do this with your 60amp. panel you have.
Question is do we ignore the calculations because we feel the actual load will never exceed the 60amp.