B bereaelectric Member Location ohio Jul 1, 2025 #1 if I install a homeline 50 amp 2 pole breaker for a rv is it going to trip with single pole loads ? [ 120 v adapters or 120 lighting loads, microwave etc.
if I install a homeline 50 amp 2 pole breaker for a rv is it going to trip with single pole loads ? [ 120 v adapters or 120 lighting loads, microwave etc.
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Jul 1, 2025 #2 No, as long as it's wired correctly. The neutral is included in the GFCI's current sensing.