i installed a new circuit in a relatively new homeline panel recently. there were no spaces left so i went to the truck and pulled out a 20/20 tandem breaker to free up a space. the only problem was i couldn't find a spot on the bus bar that would allow for the shorter slot on the breaker. i know that i have installed them in homeline panels before and that some panels only have certain spots you can put them. what am i missing here?
I actually had to call Square D on this one.
There are standard HOM breakers, and HOMT breakers... yes T for tandem.
Square D says that any panel that states 20/20 or 30/30 or 40/40 will not take a Tandem breaker. The first number is for spaces, second number is for number of breakers.
A 20/30 means 20 spaces and 30 breakers. So, only the last few spots have the Tandem ability. Same with a 30/40.
I got a 40/40 once. I needed 42 spots... it wouldn't work, and the inspector knew about the space limitation anyway.
Hope that helps.
By the way, don't modify the breaker to make it fit. It IS easy enough, but just not worth the hassle... or inspector issue... or insurance issue.