Dustyswartz
- North dakota
- Electrician
Is there any code that says a homes main distribution panel has to be attached to the home itself? Can a home have its main distribution panel in a detached garage?
There is no house yet. So I'm bringing power from the pole to the meter which will be on the garage. Then into the 200 amp panel in the garage which will eventually feed a house that will be detached.The house has it's own panel?
Your setup is fine. As mentioned you'll need a 4 wire feeder to the house panel and a disconnecting means at the house. Also needs its own GES.There is no house yet. So I'm bringing power from the pole to the meter which will be on the garage. Then into the 200 amp panel in the garage which will eventually feed a house that will be detached.
assuming the size of the service entrance conductors are based on 310.12, would you apply 310.12 C ?You won’t be able use use the reduced size of 83% on feeders from garage to house. IE, for 200 amps you will need 250 Al.
I would put a 200 amp panel in garage with feedthrough lugs to be able to route 200 to the house as well.
There is no 310.12 in my 2017. 310.15 B 7 states it has to be the entire load. But in reading this again, its a feeder so the reduced ampacity may be allowed. Lets see what others sayassuming the size of the service entrance conductors are based on 310.12, would you apply 310.12 C ?
The only way I could see that you wouldn't be able to use the 83% factor on the feeder from the garage to the house is if (a) you decide the garage load is associated with the dwelling unit (not 100% clear to me either way) and (b) the feeder rating is smaller than the service rating.You won’t be able use use the reduced size of 83% on feeders from garage to house. IE, for 200 amps you will need 250 Al.
310.12(C) in 2020 NEC = 310.15(B)(7)(3) in 2017There is no 310.12 in my 2017. 310.15 B 7 states it has to be the entire load. But in reading this again, its a feeder so the reduced ampacity may be allowed. Lets see what others say
83% rule aside, why would 4/0 aluminum at 75C terminations with a 190 ampacity and next size up rule to 200 amp not work? Assuming calculated load was 190 amps or less and no other conditions of use.You won’t be able use use the reduced size of 83% on feeders from garage to house. IE, for 200 amps you will need 250 Al.
Actually it's 180 amps but you're correct, the next size up rule would allow a 200 amp OCPD if the load were 180 amps or less.83% rule aside, why would 4/0 aluminum at 75C terminations with a 190 ampacity and next size up rule to 200 amp not work? Assuming calculated load was 190 amps or less and no other conditions of use.
Good point. The OP could just use a 200 amp feed thru panel and use conductors the same size as the service reduced size service conductors. But I was thinking that the OP was going to use , say, a 150 feeder to the house which would not qualify for the 83% rule.Remember that feeder conductors need not be larger than the service conductors.
It would if you consider the detached garage not to be a load "associated with an individual dwelling unit." The feeder to the house would still be supplying the "entire load" of the dwelling unit in that case.But I was thinking that the OP was going to use , say, a 150 feeder to the house which would not qualify for the 83% rule.