JasonCo
Senior Member
- Location
- Houston, Texas
I have a few homework questions that ask what size fuses I'll need for the scenarios it gives. I'll just spit out one example, and then will try and solve it, am just hoping to get feedback on if I'm doing it right, or how to do it if I'm not!
Scenario: A fused safety switch feeds a 480 to 208Y/120-v, 3phase, 30 KVA transformer. The transformer supplies power to a 3phase 100-amp main breaker panelboard. According to NEC 450.3, the fuses in the safety switch are permitted to be not larger than ___ amps so that the transformer is adequately protected against overload.
---------------------------------
Okay, so I assume I need to find amps. Amps for 3 phase is Power (30,000) / (208 x 1.732) = 83.27 amps
I assume the answer is 90 amp fuse..
Also, looking at table 450.3(B), does this table apply to this question? It is under 1000v and the amps is 83 amps so its over 9 amps (shown in the table), which says 125%... Idk if any of that even applies to this question, just curious! Really appreciate your time and help on this question!
Scenario: A fused safety switch feeds a 480 to 208Y/120-v, 3phase, 30 KVA transformer. The transformer supplies power to a 3phase 100-amp main breaker panelboard. According to NEC 450.3, the fuses in the safety switch are permitted to be not larger than ___ amps so that the transformer is adequately protected against overload.
---------------------------------
Okay, so I assume I need to find amps. Amps for 3 phase is Power (30,000) / (208 x 1.732) = 83.27 amps
I assume the answer is 90 amp fuse..
Also, looking at table 450.3(B), does this table apply to this question? It is under 1000v and the amps is 83 amps so its over 9 amps (shown in the table), which says 125%... Idk if any of that even applies to this question, just curious! Really appreciate your time and help on this question!