Hood Fan
Can a hood fan that is Hard Wired be connected to the required 210.11(C)(1) small appliance branch circuit?
Did you go to 210.52(B) that was referenced in 210.11(C)(1)?
There it tells you what outlets are to be served and then says it shall serve no other outlets.
Are you saying the branch circuit conductors extending from the box to the hood are an "outlet"?
Depends on the interpretation, but generally where the connection is (where current is being taken from, not where it ​could be) is where the outlet is making Alwons answer the better answer....
VVVVVVVVVV
The connection in the hood is the outlet.
However, even if boxed wires or nm whip wasn't being connected to anything at all- it could still be a violation based solely on the fact its being fed by the SABC outside of area specified to be SABC. Kind of like the receptacle directly opposite the kitchen in another room that is connected to an SABC.