I normally do maintenance so I don't get too much hands on experience ordering material.
Located in Nunavut, in a small remote hamlet so I don't have access to an electrical wholesaler and everything needs to be figured out on what is needed then ordered then shipped or flown in.
The pressure washer draws 85 amps 208 V 3phase (from the specs label).
The pressure washer is located in a garage between bays and will be used to clean trucks and heavy equipment.
The manual advises that it be on a GFCI, or a twist-lock connection or hardwired.
Hardwired isn't really a good option since I'd need to run the Teck cable overhead and down to the pressure washer.
I've chosen to use SOOW with Hubble pin and sleeve connector/socket so that the cable can be rolled up when the machine isn't in use.
I've planned on a 100 amp 3P breaker and 60 feet of Teck cable to a 100 amp disconnect with an attached pin-sleeve 100 amp receptacle.
On site we have 3C #3 AWG Teck cable. Wo don't have the SOOW cable although in our system inventory database it list 4C #2 AWG SOOW.
My questions are:
can I use #3 Teck cable up to the disconnect then # 2 for the cab tire or do I need to stick to all one size AWG?
Does the disconnect need to be fused?
Thanks in advance...
Located in Nunavut, in a small remote hamlet so I don't have access to an electrical wholesaler and everything needs to be figured out on what is needed then ordered then shipped or flown in.
The pressure washer draws 85 amps 208 V 3phase (from the specs label).
The pressure washer is located in a garage between bays and will be used to clean trucks and heavy equipment.
The manual advises that it be on a GFCI, or a twist-lock connection or hardwired.
Hardwired isn't really a good option since I'd need to run the Teck cable overhead and down to the pressure washer.
I've chosen to use SOOW with Hubble pin and sleeve connector/socket so that the cable can be rolled up when the machine isn't in use.
I've planned on a 100 amp 3P breaker and 60 feet of Teck cable to a 100 amp disconnect with an attached pin-sleeve 100 amp receptacle.
On site we have 3C #3 AWG Teck cable. Wo don't have the SOOW cable although in our system inventory database it list 4C #2 AWG SOOW.
My questions are:
can I use #3 Teck cable up to the disconnect then # 2 for the cab tire or do I need to stick to all one size AWG?
Does the disconnect need to be fused?
Thanks in advance...