bakerbrotherselectric
Member
Hooking up a spa with a all-in-one GFCI 50 amp breaker/disconnect. I've had the understanding that the disconnect needs to be located within 5 to 10' of the inside wall of the spa. The first contractor told the customer that it needed to be located at 50' from the spa, which he planned on installing on the house? This I was not aware of. So looking at the code, 680.12, it states: and shall be located at least 1.5m(5') horizontally from the inside walls of the pool, spa, or hot tub unless separated from the open water by a permanently installed barrier that provides a 1.5m reach path or greater.
So reading this I understand that it needs to be located at least 5' away, but what would be the maximum distance the disconnect can be located? Is it legal to mount the disconnect 50' away from the spa? The only spot I can find the maximum distance is on the disconnect package itself. The package states that the NEC requires a disconnect switch within 10' of the spa. If someone can clarify this for me it would be greatly appreciated.. Thanks
So reading this I understand that it needs to be located at least 5' away, but what would be the maximum distance the disconnect can be located? Is it legal to mount the disconnect 50' away from the spa? The only spot I can find the maximum distance is on the disconnect package itself. The package states that the NEC requires a disconnect switch within 10' of the spa. If someone can clarify this for me it would be greatly appreciated.. Thanks