240.33 of the 2002 NEC allows circuit breaker enclosures to be installed horizontally where in accordance with 240.81
240.81 states "Where circuit breaker handles are operated vertically rather than rotationally or horizontally, the "up" position of the handle shall be the "on" position.
Does this mean that a typical panelboard that is normally mounted vertically with two rows of horizontal breakers are not permitted to be installed horizontally? In this case, one row would not meet this requirement.
However, panelboards that have vertically installed breakers that become horizontal when the panel is mounted horizontal are allowed per this section?
Please clarify?