Leo1
Member
- Location
- Los Alamos, NM
When are we required to use the horsepower rating of a safety switch versus its amperage rating? For example if a 600hp motor with an integral solid state starter has a FLA current of the motor is 652 AMP, then at 125% that is 815 AMP for service conductors and main disconnect switch. For 480VAC, 3 phase safety switches I would select a 1,200 AMP safety switch and fuse it at 900 AMP. This all seems correct but I have a question, "The rating of the most safety switch at 1200 amps is 500 hp"? Is this a concern? I think not since the 600hp motor has a starter. Correct?