NEC 517.31(B) states the following:
And NEC 517.31(C)(1) states this:
The way that sounds to me is that if your EES is 150kVA or less, you can have one transfer switch to feed the three different branches (LS, CB and EB), but with the separation of circuit limitations, you can't actually connect the EB to the load side of the transfer switch -- not without violating 517.31(C)(1). There is an exception to allow combination between LS and CB "in transfer equipment enclosures," but this exception does not include EB.
So my question is this -- where are you legally allowed to tie in your EB wiring/feeder on this type of system? The Informational Note Figure 517.31(b) shows it diagrammatically, but the associated text does not seem to allow it this way.
One transfer switch and downstream distribution system shall
be permitted to serve one or more branches in a facility with a
maximum demand on the essential electrical system of 150 kVA.
And NEC 517.31(C)(1) states this:
Separation from Other Circuits The life safety branch
and critical branch of the essential electrical system shall be
kept entirely independent of all other wiring and equipment and
shall not enter the same raceways, boxes, or cabinets with each
other or other wiring....
Wiring of the life safety branch and the critical branch shall
be permitted to occupy the same raceways, boxes, or cabinets of
other circuits not part of the branch where such wiring complies
with one of the following:
(1) Is in transfer equipment enclosures
(2) Is in exit or emergency luminaires supplied from two
sources
(3) Is in a common junction box attached to exit or emergency
luminaires supplied from two sources
(4) Is for two or more circuits supplied from the same branch
and same transfer switch
The wiring of the equipment branch shall be permitted to
occupy the same raceways, boxes, or cabinets of other circuits
that are not part of the essential electrical system.
The way that sounds to me is that if your EES is 150kVA or less, you can have one transfer switch to feed the three different branches (LS, CB and EB), but with the separation of circuit limitations, you can't actually connect the EB to the load side of the transfer switch -- not without violating 517.31(C)(1). There is an exception to allow combination between LS and CB "in transfer equipment enclosures," but this exception does not include EB.
So my question is this -- where are you legally allowed to tie in your EB wiring/feeder on this type of system? The Informational Note Figure 517.31(b) shows it diagrammatically, but the associated text does not seem to allow it this way.