B baluiyer Member Location Pleasant Prairie, WI USA Jan 29, 2007 #1 Can we use un-shielded control cables in Hospital security, lighting, elevator and HVAC systems? Balu Iyer
Can we use un-shielded control cables in Hospital security, lighting, elevator and HVAC systems? Balu Iyer
B bmac71 Member Jan 29, 2007 #2 The way I am reading this you cannot. See Art: 517.74 (B) which refers you to Art: 725.27 which states the insulation shall be suitable for 600 volts.
The way I am reading this you cannot. See Art: 517.74 (B) which refers you to Art: 725.27 which states the insulation shall be suitable for 600 volts.