S scottysolar Member Mar 22, 2018 #1 is hospital grade mc ap steel cable acceptable for emergency circuits in a hospital
roger Moderator Staff member Location Fl Occupation Retired Electrician Mar 22, 2018 #2 scottysolar said: is hospital grade mc ap steel cable acceptable for emergency circuits in a hospital Click to expand... Generally speaking no it's not, see 517.30(C)(3) Roger
scottysolar said: is hospital grade mc ap steel cable acceptable for emergency circuits in a hospital Click to expand... Generally speaking no it's not, see 517.30(C)(3) Roger
roger Moderator Staff member Location Fl Occupation Retired Electrician Mar 22, 2018 #4 scottysolar said: refers you to 517.13 a & b Click to expand... Yes it does but it doesn't change the requirement of mechanical protection covered in 517.30(C)(3), it simply states that if it's a branch circuit it will ALSO comply with the requirements of 517.13(A)&(B) Roger
scottysolar said: refers you to 517.13 a & b Click to expand... Yes it does but it doesn't change the requirement of mechanical protection covered in 517.30(C)(3), it simply states that if it's a branch circuit it will ALSO comply with the requirements of 517.13(A)&(B) Roger