- Electrical Engineer, PE
517.30 C(3) states
So the first sentence states that all emergency wiring shall be mechanically protected but the second sentence makes it only apply to patient care areas. We are currently designing a pharmacy so the question is what wiring method is required.
The wiring of the emergency system in hospitals shall be mechanically protected. Where installed as branch circuits in patient care areas, the installation shall comply with the requirements of 517.13(A) and (B). The following wiring methods shall be permitted:
So the first sentence states that all emergency wiring shall be mechanically protected but the second sentence makes it only apply to patient care areas. We are currently designing a pharmacy so the question is what wiring method is required.