Long time lurker here, first time poster.
The project is a medical facility that has been operational for less than two years, but has ramped up its use within the last six months. With this ramp up, the user has reported an increase in random tripping of GFCI receptacles in a couple of specific rooms. Some background on what we've discovered so far:
- The tripping has been completely random, and we've not been able to identify a specific piece of equipment as the culprit.
- Tripping seems to occur at start-up; for example, the user will plug something in, hit the "on" button, and seconds later, a trip.
- The electrician has tested receptacles and confirmed no issues with branch circuitry/installation. They've even replaced all of the receptacles in the rooms, but some of these receptacles have tripped as well.
- GFCI receptacles in other rooms have not experienced issues; the rooms with the issues are fed from a panel that is dedicated to the rooms (the panel feeds no loads outside of these rooms).
This one has been a real head scratcher, so any feedback/input would be appreciated. Has anyone seen line side power issues causing a GFCI to trip, or can the issue only be on the load side? Thanks in advance!
The project is a medical facility that has been operational for less than two years, but has ramped up its use within the last six months. With this ramp up, the user has reported an increase in random tripping of GFCI receptacles in a couple of specific rooms. Some background on what we've discovered so far:
- The tripping has been completely random, and we've not been able to identify a specific piece of equipment as the culprit.
- Tripping seems to occur at start-up; for example, the user will plug something in, hit the "on" button, and seconds later, a trip.
- The electrician has tested receptacles and confirmed no issues with branch circuitry/installation. They've even replaced all of the receptacles in the rooms, but some of these receptacles have tripped as well.
- GFCI receptacles in other rooms have not experienced issues; the rooms with the issues are fed from a panel that is dedicated to the rooms (the panel feeds no loads outside of these rooms).
This one has been a real head scratcher, so any feedback/input would be appreciated. Has anyone seen line side power issues causing a GFCI to trip, or can the issue only be on the load side? Thanks in advance!