Article 517.13.A is saying we are required to run a listed raceway system or metallic cable armor, or sheath assembly that is rated to qualify as a equipment ground in accordance with 250.118. In addition to this, (article 517.13.B) requires a insulated grounding conductor ran integral to the run.
These are required in patient care areas.
Couple questions
With all that being said, it definitely indicates that we are to run a redundant ground in all patient care areas(well, excluding the exceptions). Does that mean, if we are running a Hospital grade MC(with redundant ground), do we need to run hospital grade MC back to the panel, if the home runs are not in patient care area? Or can we get away with regular MC?
Furthermore, if I read this right, it sounds like we can't run PVC, or Smurf in deck as home run conduits that serves patient care? area?
These are required in patient care areas.
Couple questions
With all that being said, it definitely indicates that we are to run a redundant ground in all patient care areas(well, excluding the exceptions). Does that mean, if we are running a Hospital grade MC(with redundant ground), do we need to run hospital grade MC back to the panel, if the home runs are not in patient care area? Or can we get away with regular MC?
Furthermore, if I read this right, it sounds like we can't run PVC, or Smurf in deck as home run conduits that serves patient care? area?