S scottysolar Member Mar 22, 2018 #1 where would this cable be required (type a/c for normal circuits)
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Mar 22, 2018 #2 Hospital grade MC is an acceptable wiring method for 517.13 applications (patient care areas)
Coppersmith Senior Member Location Tampa, FL, USA Occupation Electrical Contractor Mar 22, 2018 #3 augie47 said: Hospital grade MC is an acceptable wiring method for 517.13 applications (patient care areas) Click to expand... I watched a fellow contractor hang his head as the inspector told him he would have to rip out all of the MC he installed in a patient care area and replace it with hospital grade. Acceptable and required.
augie47 said: Hospital grade MC is an acceptable wiring method for 517.13 applications (patient care areas) Click to expand... I watched a fellow contractor hang his head as the inspector told him he would have to rip out all of the MC he installed in a patient care area and replace it with hospital grade. Acceptable and required.
kwired Electron manager Location NE Nebraska Occupation EC Mar 24, 2018 #4 scottysolar said: where would this cable be required (type a/c for normal circuits) Click to expand... Is not required anywhere. Is permissible in 517.13 applications as mentioned. Is acceptable for anywhere else you would use similar AC/MC cable.