Hospital Grade Receptacles

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
We have a job in a psych center. The schedule and specification lists spec grade receptacles but they are saying we have to use hospital grade per NEC. Is that correct?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Unless they have "Patient Beds" (sleeping or procedure beds) or are under Anesthetizing locations HG receptacles are not required. See 517.18(B) 517.19(B)(2) and 517.61(C)(2)
 