Hospital grade receptacles would be required if the area is deemed critical care, otherwise no.
This would require redundant grounding per 517.13 by 517.10 applicability
Also check with the equipment manufacturer, some require hospital grade receptacles
Hospital grade receptacles are required by 517.18(B) for general care areas, 517.19(B)(2) for critical care areas and 517.19(C)(2) for operating rooms.Hospital grade receptacles would be required if the area is deemed critical care, otherwise no. ...
Hospital grade receptacles are required by 517.18(B) for general care areas, 517.19(B)(2) for critical care areas and 517.19(C)(2) for operating rooms.
I wasn’t aware that critical care was the distinguishing criteria determining hospital grade was required.
Are you saying hospital grade is not required in general care?
You are correct.Read the definition of patient bed location........Let me know if I'm wrong.