Hospital - Patient Bathrooms

Status
Not open for further replies.

Moedog

Member
Location
Green Bay, Wisconsin
Occupation
Electrical Designer
Question:
  • Do I need a separate circuit for a patient room bathroom GFCI receptacle, because of hair dryer use? Or is this rule just for residential purposes? Reason I’m asking is because I have never done this before in my designs. And he hired a senior electrical engineer who insists that we need to do this. Any help would be greatly appreciated.
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
If the space is not considered a 'Dwelling Unit' then your senior engineer is wrong see 210.11(C)(3) . If you talking about those permanent wall mounted hair dryers like in hotels then maby depending on the nameplate, see 210.23(A)(2)
 