What is the difference between HCF-90 and HCF-Lite. The spec sheet for the HCF-Lite says "HCF cables may not be used on emergency circuits in health care setting". I dont know if the HCF-90 is allowed to be used on emergency circuits.
NEC 517-30 (C)3 indicates that emergency branch circuit wiring shall be installed in non flexable conduit. After exception 5 is a FPN to 517.13 which allows AC cable however the explanation in the NEC Handbook clearly says that metal sheathed cable assemblies are not permitted for emergency circuits in the patient vicinity.
How are so many contractors being allowed to install HCF for emergency branch circuits in hospitals? Or am I intrepreting incorrectly?
NEC 517-30 (C)3 indicates that emergency branch circuit wiring shall be installed in non flexable conduit. After exception 5 is a FPN to 517.13 which allows AC cable however the explanation in the NEC Handbook clearly says that metal sheathed cable assemblies are not permitted for emergency circuits in the patient vicinity.
How are so many contractors being allowed to install HCF for emergency branch circuits in hospitals? Or am I intrepreting incorrectly?