Hospitals

Status
Not open for further replies.

122864

New member
An inspector is telling me that the only approved wiring method for a fire alarm system in a hospital is to put it in EMT and to look into article 517. I can not find it,can someone tell me where to look. I thought you could run either emt or hospital grade MC.

Thanks,
Alex
 

tonyi

Senior Member
Re: Hospitals

Originally posted by 122864:
An inspector is telling me that the only approved wiring method for a fire alarm system in a hospital is to put it in EMT and to look into article 517. I can not find it,can someone tell me where to look. I thought you could run either emt or hospital grade MC.

Thanks,
Alex
517.30(C)(3)

Fire alarms are part of life safety branches.

Hospital grade MC :confused: Do you mean HCF?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: Hospitals

Alex, is it a state or local code?

As far as the NEC and NFPA 99 is concerned, (depending on the system voltage) you don't need any conduit or metalic protection.

You would have to use an approved cable type per 760

As Tony points out, read 517.30(C) exception #2

This is also in NFPA 99 4.4.2.2.4.6

Roger

[ October 11, 2003, 01:44 PM: Message edited by: roger ]
 