Hot backfeed breaker

Status
Not open for further replies.

JoeNorm

Senior Member
Location
WA
Solar backfeed breakers are interesting because they are commonly operating at their max ratings for long periods of time.

Today I had a situation where I was feeding two panels side by side with the same sized array. I measured amp output of each array to be within one amp.

One of the breakers was hot to the touch, too hot to hold a finger on for more than a few seconds. The other was just warm. I found this interesting as both breakers and panels are brand new.

How hot is too hot for a breaker to be? At what point is a hot breaker a concern?

thanks
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
That's too hot. You should check the condition of the stabs and the wire terminals. You might need a new breaker in a different pair of spaces.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
If it is too hot for a sustained touch, you can be pretty sure that the thermal trip curve has also been shifted to a more sensitive position, which may also lead to nuisance trips.
 