I hope someone can help me.. I installed a 14KW generator with a 200 amp service rated ATS, when I finished the install and went to bond the unit my helper noticed the the existing ground rods for the 200 amp service was energized with 120 volts to ground. Meaning if you took a tested to the ground rod and to the bond wire or to both ground rods there was 120 volts, I proceeded to check the ATS and I had nothing unusu:?:?al I didn't have 120 volts to ground any where in the ATS, I even eliminated the existing ground wire from 200 amp service in the ATS and I still had 120 volts to ground at ground rods ??? My helper shorted out two control wires by accedent for N1,N2 and T1 which has fuse protection and blew the fuses, at this time I check the ground rods and I didn't have 120 volts, is this a coincedence, today i'm replacing the fuses, and hoping there is no voltage to ground, but i don't have a good feeling about this... What could be the problem ???