Twoskinsoneman
Senior Member
- Location
- West Virginia, USA NEC: 2020
- Occupation
- Facility Senior Electrician
Was talking to an electrician the other day. On a 480 sub panel he had a b-phase wire of the feeder way over heated. Could barely touch the wire for more than 2 seconds. He checked the voltage across the main breaker. The drop across the b phase of the breaker was twice the "a" and "c" phases but it was only 5 millivolts. He ordered a new breaker. (very expensive).
I asked what the current differences were and he said he didn't check. He said the voltage drop confirms the breaker is bad... Anyway can a 5 millivolt drop really confirm this to be a bad breaker? I am dubious but this guy has much more experience than me and I thought I would ask here.
BTW he is still waiting for the breaker to come in so I don't know what came of it yet.
I asked what the current differences were and he said he didn't check. He said the voltage drop confirms the breaker is bad... Anyway can a 5 millivolt drop really confirm this to be a bad breaker? I am dubious but this guy has much more experience than me and I thought I would ask here.
BTW he is still waiting for the breaker to come in so I don't know what came of it yet.