New construction, 600 amp main breaker removed by electrical contractor to be bench tested by testing company and replaced by same electrical contractor in 2016.
Also as part of the project infrared inspection was performed in 2019, no issues were found.
Loads on panel; basement sump pumps, exhaust fans, FCU, two transformers (maybe 100 amps max).
"A-Phase" shows gaps between breaker line side lug to bus hardware and bolt/washer to breaker lug.
I spot checked temperature upon finding loose connection and recorded temperature of 245F, molten metal at loose connection.
"B & C"- Phase" do not show any issues.
Contractor says this problem was not the cause of poor workmanship by their doing; your thoughts?