I had a GE 200 A 1 phase fused disconnect in front of a main lug only 200 A panel. Indoor on a commercial building in the Houston,TX area. Ever since A/C season has begun, the A phase conductor was getting hot on the line side at the termination, transfering the heat to the 200 A fuse and blowing the fuse. The hotter it has gotten the faster it was blowing fuses. It was an older disconnect being fed by 3/0 TW copper. Before we replaced it a thermal camera showed the conductor running 178 degrees.
We replaced the disconnect with a 200 A main breaker enclosure and new 3/0 THHN/THWN-2 copper feeders. The same thing is happening again, on the same phase and at the same termination.
When this first started happening I checked voltage, good at 120 v and only 1 volt imbalance to B phase. Checked amperage for a decent period and never saw more than 115 amps on The problem phase. Also, there,s only one A/C condensor on the panel.
Any ideas on where to look next ?
Thanks
We replaced the disconnect with a 200 A main breaker enclosure and new 3/0 THHN/THWN-2 copper feeders. The same thing is happening again, on the same phase and at the same termination.
When this first started happening I checked voltage, good at 120 v and only 1 volt imbalance to B phase. Checked amperage for a decent period and never saw more than 115 amps on The problem phase. Also, there,s only one A/C condensor on the panel.
Any ideas on where to look next ?