This is a three phase 208 volt feeder from a 225 amp breaker to an old disconnect for a HVAC split system. The old disconnect is fused down to 200 amps and feeds the condensing unit. A 20 amp circuit was run from the CU to the fan coil illegally hot tapped the distance is 30 to 40 feet. No fuses in the CU.
We need to remove the switch and feed new CU and FCU.
New CU is max fuse 60 amps, new FCU is max fuse 20 amps.
I propose removing the old switch, and installing a troff then installing two fused disconnects under the troff. One will be 60 amps the other a 30 amp with 20 amp fuses.
I want to install tap blocks in the troff and run #6 to feed each new switch then run #6 to the CU and #12 to the FCU.
Did I break any hot tap rules?