Hot to ground too High

Location
San Diego
Occupation
Electrical contractor
My company builds Jersey mikes sandwiches stores throughout southern Cali We got a service call GFCI outlets keep burning out During testing we found:
Hot to Neutral 120 volts
Hot to ground 200 Volts
Any Ideas on what could cause this ?
 
Location
San Diego
Occupation
Electrical contractor
The problem was the bread oven appliance something in the internal components was sending 200 volts back to the panel on the ground we disconnected the bread oven and everything went back to normal Thanks
 
Location
San Diego
Occupation
Electrical contractor
There is other sensitive equipment in the store but for some odd reason the 200 volts to ground was only burning up GFCI devices on the one circuit
 
Location
San Diego
Occupation
Electrical contractor
This reminds me of a job I did about a year ago. It was a large multi million dollar house that the electricity was acting crazy I had never seen anything like it. I was even having issues at the pool house that was a different structure different panel. We were trying to figure out what happened and passed by an old garage fridge that was making a unforgettable noise we unplugged it and all the issues were gone
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The problem was the bread oven appliance something in the internal components was sending 200 volts back to the panel on the ground we disconnected the bread oven and everything went back to normal Thanks
That should not be possible if the main bonding jumper is installed
There is other sensitive equipment in the store but for some odd reason the 200 volts to ground was only burning up GFCI devices on the one circuit
That also should not be possible as the GFCI device only sees the voltage between the hot and the neutral.

Something else is going on here.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Is the source of the power directly from a power co. transformer or is it fed from a distribution room such as in a mall ?
 

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent
Not buying your "solution." This is very simple. Draw it out. You have an open neutral somewhere. Next step. Check hot to hot. 208 or240 volts means shared neutral with another phase coming in. 120v same phase and likely same circuit. You have to start by finding where the neutral starts sharing with the neutral for the oven. Could be a miswired box. I am assuming the bread oven is 120 volts. but even if it is 208 volts, if it was sending 200 volts back across the neutral, that current would go back to the service on the neutral, it would loop back out of a panel to a GFCI on another circuit.
 