- Location
- Reno
I installed a sub panel for a hot tub today. It is a Homeline 125A 12/24. It has a 60 amp main breaker. It is installed on a detached cinderblock wall. Th wall conceals the pool equiptment. It is a natuaral gas fired hot tub. The cinder block wall is L shaped. Inside of the L, I found some rebars stubbed up. I asked the super if this is where I bond to the grid. He said no, bond to this 8 AWG thwn protruding through a 1 inch PVC stubbed up nearby.
I have two questions.
Was it necessary to beat down the ground rod I drove today? Would bonding to the # 8 have been sufficient?
Is a # 8 large enough to act as my GEC, for the grid?
The initial EC was fired. We inherited this job as a T & M project. The sub panel was supposed to be 100 amps, but the feeder wasn't large enough. I have already down-sized the breaker.
I have two questions.
Was it necessary to beat down the ground rod I drove today? Would bonding to the # 8 have been sufficient?
Is a # 8 large enough to act as my GEC, for the grid?
The initial EC was fired. We inherited this job as a T & M project. The sub panel was supposed to be 100 amps, but the feeder wasn't large enough. I have already down-sized the breaker.