Hot tub disconnect

Status
Not open for further replies.
I have a single family dwelling hot tub to install and there is a outside panel that that is the service disconnect for the house it is 10 ft from the tub and within sight. Is it code compliant to install a gfci breaker in that panel for the disconnecting means? Or do I need a dedicated spa panel?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I see no reason a GF breaker in the service panel would not be compliant.
 