Per the Newsletter Question 12 brings another question after I recieved the answers.
Q12. I have a hot tub disconnect located fifteen feet from a hot tub and it?s plainly visible from the tub. Someone told me that the disconnect is required to be visible from the motor as well. Is this true?
A12. No. The maintenance disconnecting means for hot tubs must be readily accessible and located within sight and at least 5 ft from the hot tub unless separated from the open water by a permanently installed barrier that provides a 5 ft reach path or greater. This horizontal distance is measured from the water?s edge along the shortest path required to reach the disconnecting means [680.12].
I was under the impression the disconnect should be within sight from the equipment to be serviced (motor, controls, ect.) If the tub was sunken in a deck would the disconnect be needed at the top level visible from the tub or below the deck for the servicing of the equipment?