50 amp QO GFCI breakers have a neutral.sorry for mistakes but this is because of quick typing and English is not my first language .
This is what he told me : because breaker doesn't have a "spot" for load neutral, hot "tube" ;-) will not have line to neutral protection.
Is this sound right?
I used the breaker as on the picture.
We are using square d panel. Only this breaker fit there, and this breaker doesn't have load neutral termination.
Why i can't have both neutral connected to a neutral bus bar?
According to the catalog only the 60 amp version is missing the load neutral termination. If you do have what appears to be a 50 it may be an assembly error at the factory.I used the breaker as on the picture.
We are using square d panel. Only this breaker fit there, and this breaker doesn't have load neutral termination.
Why i can't have both neutral connected to a neutral bus bar?
Picture looks like a 60 to me, but it's hard to read.
I used the breaker as on the picture.
We are using square d panel. Only this breaker fit there, and this breaker doesn't have load neutral termination.
Why i can't have both neutral connected to a neutral bus bar?
Picture looks like a 60 to me, but it's hard to read.
The picture is 60A and it looks like something copied from a website, if not the OP is very good at editing out the background.
Giveaway that it possibly has never been installed before.Good point. The still perfectly coiled neutral is also a giveaway.