I installed a Siemens 2 pole 50 Amp GFCI breaker in a main residential panel. I connected the breaker neutral pigtail to the neutral bar, which is also tied in as a grounding bar. This panel is the first means of disconnect(main breaker, 200 Amp). From here, I ran 2-#6 & 1-#10 THHN conductors(2 hot/1 ground, all insulated)to an outdoor 60 Amp non-fused disconnect. From the disconnect, I continued to the hot tub, all in 3/4" PVCEC Schedule 40. The tub unit is an old 220 volt system with no neutral connection in the control panel. The panel skematic & the wiring itself contain black, red, white & green conductors. There are also lights & a device that
looks like a small transformer. There are no signs of a neutral wire on the terminal block. The developed length from the GFCI breaker to the tub is aprox. 50'. Why does the GFCI breaker always trip. It acts like a ground to neutral tripping. Other electricians have had this same problem, but no one can say why.
looks like a small transformer. There are no signs of a neutral wire on the terminal block. The developed length from the GFCI breaker to the tub is aprox. 50'. Why does the GFCI breaker always trip. It acts like a ground to neutral tripping. Other electricians have had this same problem, but no one can say why.