Hot Tub Grounding

Status
Not open for further replies.
The answers are no and no. You need to review Article 680. Particularly look at Part IV.
 
mikeomie1918 said:
Do i have to use a ground rod or can i rely on the conduit as the ground to the gfi, connected to the house panel.

A ground rod is unnecessary and virtually useless. If you are running conduit then you must use an insulated ground as your EGC.

I am confused by your question of "can i rely on the conduit as the ground to the gfi" The conduit nor the ground gets connected to the GFCI.

Read 680 part IV as Trevor suggested
 
Just some things to consider.

Is this a structure?

hot-tub.jpg


Is it 'separate'?

Does it have a feeder running to it?

250.32(A)
 
iwire said:
Just some things to consider.

Is this a structure? Picture of Hot Tub-- saving space

Is it 'separate'?

Does it have a feeder running to it?

250.32(A)

That is a very valid question and one I know we can argue forever. I can only add that I have never been required to add a ground rod so either everyone here is not considering it a structure or they never even thought about it.
 
Dennis Alwon said:
or they never even thought about it.

That would be my bet.

There is no way that hot tub in the photo is not a 'structure' by NEC definition.

It was without a doubt built or constructed.
 
Last edited:
Here is another take on it. Do you suppose the wire we run is just a branch circuit that feeds a factory assembled unit and it is not a feeder. Does the fact that the factory assembly has OCP determine if our wire becomes a feeder ???? :confused:
 
Dennis Alwon said:
Here is another take on it. Do you suppose the wire we run is just a branch circuit that feeds a factory assembled unit and it is not a feeder. Does the fact that the factory assembly has OCP determine if our wire becomes a feeder ???? :confused:

I understand exactly what your saying and honestly I am not sure of the answer.
 