Hot tub load calculations

Status
Not open for further replies.

Sykes81

New member
When doing load calculations for a single family dwelling (either standard or optional methods) what is a 9500 VA hot tub calculated at? Is it with appliances? Is it taken at 100%? Article 680 isn't too clear on this nor is 220.
 

RRelec

Member
Location
Florida Keys
Sykes81 said:
When doing load calculations for a single family dwelling (either standard or optional methods) what is a 9500 VA hot tub calculated at? Is it with appliances? Is it taken at 100%? Article 680 isn't too clear on this nor is 220.

I would in a standard calculation, include the load per 220.14 (A) @ 100%. However, If the A/C compressor is not the largest motor and the hot tub motor is, I would add the 25% of the motor. Also assuming that the hot tub motor is the largest motor on the feeder.

If using the optional method, meeting 220.82 (A) requirements, I would use 100% and include it as part of 220.82 (B) (4).

Just my thoughts,
R
 