electricrulez247
We just did the electrical installation of a Self-contained Hot Tub on a existing concrete porch outside. The deck is 15 feet above grade has a steel frame with metal decking with concrete poured on top. We bonded the steel frame of the deck to the metal frame of the hot tub. Our AHJ had no problem with this, but we talked about if this had been a new concrete deck built to set a hot tub on then the requirements of 680.26(C) Equipotential Bonding Grid would apply. He cited 680.42 Outdoor Installations of Spas and Hot Tubs shall comply with the provisions of Part I and II of this article (680). (we use 2005 NEC)
With that in mind then any time you poured a concrete pad for a Self-contained Hot Tub, either on the ground or an "above grade deck", would require a Equipotential Bonding Grid.
We have been installing the Equipotential Bonding Grid on concrete pads poured on grade for Self-contained Hot Tubs per AHJ. The problem I have with this is the NEC in 680.26(C) is worded and written for a swimming pool. I can't see how to apply this to a Self-contained Hot Tub much less on a above grade concrete deck.
Somebody show me how 680.26(C) applys to a outdoor Self-contained Hot Tub. (in particlar one mounted on a above grade concrete deck)
All of art. 680 needs a major rewrite.