J jcapp Member May 13, 2011 #1 Im putting a hot tube directly on the ground with no concrete, pavers, or decking, just sitting on the grass. do i need some type of bonding ring or mesh?
Im putting a hot tube directly on the ground with no concrete, pavers, or decking, just sitting on the grass. do i need some type of bonding ring or mesh?
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor May 13, 2011 #2 You still need an equipotential bonding ring. Depends on what code cycle whether it needs a mesh or perimeter bonding.
You still need an equipotential bonding ring. Depends on what code cycle whether it needs a mesh or perimeter bonding.
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor May 13, 2011 #4 jcapp said: we are still using 2008 Click to expand... 680.26 will show a perimeter bond is needed.