1) ok, lets say you have a 9x9 on-grade slab with mesh, a 7x7 spa sits centered on that, you bond motor lug to mesh. the egc from sub panel has corroded and is now a 150k resistor. the bond becomes 240vac for whatever reason, you step out wet and one foot is on earth one foot is on slab.
2) take the same scenario but jab earth with a 20ft ground rod right next to slab, buried, attach bond grid to rod.
you would choose option 1 over option 2?
within NEC 680, the notion of equi bonding does not exist unless the EGC is lost. since 680 requires pool pump to have EGC connection (with most everything else within the pool/spa wiring has the egc tied to everything else that is metal), after applying the rest of 680 what you are left with is a everything that is grounded. a big system of connected EGC's that have no tie back to the supply grounded (earth) conductor is nothing more than a ungrounded equi bonded grid, like standing bare foot on a 10x10 wire mesh in the dirt. a ungrounded equi grid can still pose a hazard :thumbsup:
but look at the metal pool ladder, typically is not tied to EGC, so you bond it to the "equi grid", which is directly tied to the EGC elsewhere, thus ladder is now grounded.
the ground rod has a purpose, it provides extra safety. seems to be optional within NEC books.