Most control panels have the pump(s) included in them. All the ones I've installed did.That is the heater and control panel. It likely does not include the current drawn by pump motor(s) and accessories like an ozonator.
No idea, 40A would have been the right size. Could be the installer was used to installing 50A for tubs as that is the normal size circuit for a hot tub and just didn't read the nameplate. What size wire did they run?
That is the heater and control panel. It likely does not include the current drawn by pump motor(s) and accessories like an ozonator.
Is this a cord & plug unit?I opened it up and the SO cable is ram to
Sent from my iPhone using Tapatalk
Is this a cord & plug unit?
Yea they want a 240 but the cord is hooked up to be 120
Sent from my iPhone using Tapatalk
You would need to check and see if the tub is allowed to be cord/plug connected when run on 240V. There would have to be a circuit ran to a box with a 40 or 50A receptacle as you can't wire straight to a panel with SO cord.Yea they want a 240 but the cord is hooked up to be 120
Sent from my iPhone using Tapatalk
You would need to check and see if the tub is allowed to be cord/plug connected when run on 240V. There would have to be a circuit ran to a box with a 40 or 50A receptacle as you can't wire straight to a panel with SO cord.
You would need to check and see if the tub is allowed to be cord/plug connected when run on 240V. There would have to be a circuit ran to a box with a 40 or 50A receptacle as you can't wire straight to a panel with SO cord.
They can’t find the manual and I can’t find it online
Sent from my iPhone using Tapatalk
That's what I would do.I was going to run new wires car flex or seal tight and run it to a 50a gfci disconnect that has the breaker inside
Sent from my iPhone using Tapatalk
Yep, make sure it is within sight (50' or less) and no closer than 5' from tub.They have a j box with the 50a circuit in it. I’ll just replace the j box with a disconnect box no ?
Sent from my iPhone using Tapatalk
That's what I would do.
You also need to check and see if something like dip switches or a jumper needs to be changed to run it on 240V.
Yep, make sure it is within sight (50' or less) and no closer than 5' from tub.
Probably not if the diagram doesn't show one. Sounds like you just replace the neutral with another hot on line 2.So when I looked all I gotta do is put the other hot on line 2 to make 220 or 240.
It’s hooked up as 120v right now. Why would u need a jumper?
Sent from my iPhone using Tapatalk