Hot Tub/Spa wire Ampacity and Breaker Size

Status
Not open for further replies.

al

Senior Member
Location
Minnesota
Should the wire and breaker size be 100% of unit marked current or 125% ? I have seen many units just marked with a current rating, not the typical min circuit ampacity/max overcurrent rating like you would see on an air conditioner.

Al
 
Re: Hot Tub/Spa wire Ampacity and Breaker Size

2005 NEC:

680.9 Electric Pool Water Heaters
All electric pool water heaters shall have the heating elements subdivided into loads not exceeding 48 amperes and protected at not over 60 amperes. The ampacity of the branch-circuit conductors and the rating or setting of overcurrent protective devices shall not be less than 125 percent of the total nameplate-rated load.

This was the only thing I found that was spa-related that mentioned 125%. This section is in Part I of the article, and Part I applies to spas.

[ December 30, 2005, 11:33 AM: Message edited by: jeff43222 ]
 
Re: Hot Tub/Spa wire Ampacity and Breaker Size

Would it be safe to say that spa/hot tub would be a continuous load (+3hour), thus be figured at 125%?
 
Re: Hot Tub/Spa wire Ampacity and Breaker Size

The heater will not likely run for more than three hours without cycling off and then on again. The circulating pump will run 24/7, but that is already covered by the motor rules (in 430).
 
Re: Hot Tub/Spa wire Ampacity and Breaker Size

charlie b
Here in CT, if you change the water every three months like the instruction recommend, sooner or later you will have to it in the winter. The new water is about 55 degrees, unless you fill it with hot water but with 300 gallons I don't want to do that, in the summer its about 70 degrees. The heat-up rate is about 3 to 5 degrees per hour which means on my unit the heaters and one pump will run much longer then three hours to bring the temp back to 102 degrees. I have found this to be the case on any Hot Tub that I have wired.
Lou
 
Re: Hot Tub/Spa wire Ampacity and Breaker Size

From what I read in part IV in article 680, there is no mention of sizing to 125% so I would go by the nameplate rating for circuit sizing. I don't believe Part 1 of 680 pertains to spas or hot tubs. Please correct me if I'm wrong.
 
Re: Hot Tub/Spa wire Ampacity and Breaker Size

Thanks.....My bad. What about the circuit sizing? Is the nameplate information adequate or do we go to 125% of the rating? I can't see anything that defines this.
 
Re: Hot Tub/Spa wire Ampacity and Breaker Size

According to the Mfg. the electrical requirements are:
"230 volt, 50 amp Single phase GFCI protected circuit"

And to further complicate things the diagrams show a 50A breaker with #8 wire

How do these units ever get a listing?

They should say: minimum circuit ampacity 40A,
maximum overcuurent device 50A

[ January 04, 2006, 03:52 PM: Message edited by: al ]
 