Figured I'd get your opinions before I tell my customer to call the hot tub company. I despise hot tub service calls...but anyway;
GFCI disconnect trips almost immediately. It holds with L1 and L2 removed at the tub, it holds with only L1 or only L2 connected to either terminal. However once 240V is applied the tripping occurs. I pulled the plugs on the pumps and ozone generator, and it still trips. I'm 99% sure it's the tub and I suspect the heater, but I wanted some opinions before having the customer call the pool co.
Note: power is on long enough for a relay to engage on the tub's control board, maybe one second, and that's it.
Thanks!
GFCI disconnect trips almost immediately. It holds with L1 and L2 removed at the tub, it holds with only L1 or only L2 connected to either terminal. However once 240V is applied the tripping occurs. I pulled the plugs on the pumps and ozone generator, and it still trips. I'm 99% sure it's the tub and I suspect the heater, but I wanted some opinions before having the customer call the pool co.