What install / wire to you use:
If you have an outdoor breaker panel and you drop out of the bottom with PVC and then LB inside to the basement, then run across the basement and pop out and install an LB up with a riser into a hot tub disconnect.
Since 6-3 CU NM cannot be installed in a PVC conduit outside. What do you do? A J-box on both ends to switch from THHN to 6/3 NM is no good. Installing a raceway through the basement isnt either.
Is there a 6/3 cable that is rated to be installed in a outdoor raceway.
Sorry for the rookie question. I don't do a lot of Hot tubs