1. Circuit breaker enclosures are marked to indicate the temperature rating of all field installed conductors.
2. Circuit breakers with a current rating of 125 A or less are marked as being suitable for 60?C, 75?C only or 60/75?C rated conductors. It is acceptable to use conductors with a higher insulation rating, if the ampacity is based on the conductor temperature rating marked on the breaker.
3. Circuit breakers rated 125 A or less and marked suitable for use with 75?C rated conductors are intended for field use with 75?C rated conductors at full 75?C ampacity only when the circuit breaker is installed in a circuit breaker enclosure or individually mounted in an industrial control panel with no other component next to it, unless the end-use equipment panelboard, switchboard, service equipment, power outlet, etc.) is also marked suitable for use with conductors rated 75?C.
4. A circuit breaker with a current rating of more than 125 A is suitable for use with conductors rated 75?C.
5. Circuit breakers intended for continuous operation at 100 percent of rated current may be marked to be connected with 90?C rated wire with the size based on 75?C ampacity.